My client has two bedrooms with vaulted ceilings, 4/12 pitch, exposed 4x4 rafters 3-1/4" thick, under 1" tongue and groove boards. The ceilings are unvented and the home is located in Southern California.
My plan was to fill the cavities with Hunter H Shield panels 2 1/2". Thereby leaving a 3/4" gap of dead air. Then running full sheets of 3/4" Rmax R-Matte Plus-3 unde the rafters. Then taping the seams of the Rmax with Tyvek housewrap tape, to try and air seal as much as possible.
Also, there are 4 fiberglass jboxes in roof that will be getting LED surface lighting installed. I was planning on using fireblocking foam to surruond the jboxes.
2.5" Hunter polyiso= R15.3
3/4" dead air = R2.77
3/4" Rmax = R5
Total Rvalue = 23.07
What do you guys think?
All How-To Topics





 Uh, yeah... (post #206796, reply #1 of 1)
Uh, yeah... don't.
Look, the is alreay a nice loking finish on the underside of that deck there with the 4x and the tongue & groove. Leave it, it looks nice.
Instead, focus the efforts on the area ABOVE that deck.
Now you have a well sealed, well insulated roof (R22) and didn't have to impact the living areas at all. If you need more, you can add another 2" layer under the horizontal furring, giving you R36... but that's a little much here in mild SoCal!