15 or 20 amp?

LOSVEC's picture

I would like to replace all switches and receptacles in my house. Now my breakers are 20 amp but the old switches and receptacles are 15 amp. so my question is do I stay with the 15 amp or go up to 20 amp to match the breakers? Thank you for your replies.

Size of wire and type is what matters (post #205812, reply #1 of 3)

14 gauge stick w/ 15 amp breaker.  12 gauge use 20 amp breaker  based on COPPER wire. if unusual long runs from panel or aluminum get electritian.  My 2 cents opinion only

The code allows 15a (post #205812, reply #2 of 3)

The code allows 15a receptacles on 20a circuits as long as there is more than one. The assumption is that you probably don't have any 20a equipment anyway. (NEMA 5-20 plug)

Yeah, the switches and (post #205812, reply #3 of 3)

Yeah, the switches and recptacles may be rated for 15A.  This (in most cases) is fine on a 20A circuit.  It's basically only the wire that must be sized to handle the entire 20A.


We are like tenant farmers chopping down the fence around our house for fuel when we should be using Nature's inexhaustible sources of energy -- sun, wind and tide. ... I'd put my money on the sun and solar energy. What a source of power! I hope we don't have to wait until oil and coal run out before we tackle that. --Thomas Edison