We have an old stove wired with #3 6/G copper. Can we use that wire to install 50 amp subpanel and run a 40 amp cooktop and 20 amp wall oven off that subpanel? Thanks
Discussion Forum
Discussion Forum
Up Next
Video Shorts
Featured Story
There's a constant source of clean water for you to use, and all you have to do is collect it.
Featured Video
How to Install Exterior Window TrimHighlights
"I have learned so much thanks to the searchable articles on the FHB website. I can confidently say that I expect to be a life-long subscriber." - M.K.
Replies
If you're saying you have 3 wires + a ground wire and the size is #6. Then yes.
electrical subpanel
Thank you so much. It is a 3 wire with a ground wire that is #6. We thought it would be OK and glad to have it confirmed.